Re: Alright everyone, I need electrical upgrades, time for ALL NEW! Suggestions needed!
Posted: March 5th, 2019, 7:41 pm
Couple of notes.
Maybe they have changed the Compact panels. This is the label they were showing for them. This is the label that would normally be on the back side of the panel:
On the fusing, just keep in mind a couple of things. One is that a fuse is to protect the wire. So you can't always just up the size. I think the stock solar wire is 12AWG. If it's rated at 90ºC then you could fuse it to 40 amps, so not saying you are not safe there. Just something to keep in mind when changing fuse sizes. Also, for solar, go as large as you can to save on the voltage drop of smaller fuses. Voltage drop is the enemy.
Just for example, let's say one were to put two 100 watt panels on the original Chinook wire. Let's say you added ten feet of wire to get to the new second panel. That would be around 32' of 12 AWG, one way. Now let's say you run them in series and have 5 amps at 16 volts trundling along. The voltage drop would be 4.4% (not counting any additional wire such as battery jumpers). That would make your 16 volts into about 15.3 volts. But we also have a solar controller in there. So let's say you set your solar controller to absorb at 14.4 volts (that's a common spec for a lead acid battery in absorb). Now you have around 15' to the controller, so that voltage drop is a bummer, but doesn't actually affect your battery charging specs. It only causes you to lose some power that will never get to the controller.
But now the controller puts out 14.4 volts (if it's 77ºF) and that goes 17' to the batteries on the Chinook stock wire. That's about 2.3% voltage drop on that leg (controller to batteries). That means the 14.4 volts your batteries want (and that you set into the controller) will actually be 14.06 volts (about). That's a big difference for batteries.
None of this may matter to you. Many people just plan on replacing batteries every year or two (obviously buy relatively cheap ones) and that is a fine plan if it suits your attitude and the availability of batteries to you. Just something to be aware of.
Admittedly, I'm on the opposite end of the spectrum. I rely on my batteries for boondocking all the time, and I hate re-buying things. So I have my system set up for minimum voltage drop, have a temperature compensated controller, etc. But that's not the only way. The only time it kind of bums me out is if someone thinks they are doing "Way A," but without realizing it are actually doing "Way B." That can lead to frustration.
On the series pairs: I too always read the wisdom of not doing series if there might be any shading. However it was attractive to me for a couple of reasons: You can have longer and thinner wires (less voltage drop at higher voltage), fewer wires, and (theoretically at least), the panels will "wake up" sooner and "go to bed" later. The first advantage is huge for ground panels, as you can have a longer thinner tether for the same result. But also it's fairly easy to put them in the sun so not much to lose by going series and everything to gain.
But what about roof panels? Well, I took a pair of matching panels (135 watts each, 17.6 volts vmp) and set them out on a summer day at around noon. So good, predictable sun. I set them flat on the ground, like an RV roof would be. I hooked them up to my battery monitor and the display on my MPPT controller so I could get good info. I started up some big loads so the controller would have reason to give me everything the panels could. Then I started in with the shade. Various things I tried were thin branches about 15' away, falling in a line or two over the panels, large deciduous trees a few hundred feet away shading either small amounts of one panel or up to a third or half of one panel (more blob like shape), and then finally l placed a piece of cardboard over one or more cells on one panel.
Interestingly, the branches and the big far away trees only knocked out either part or all of the shaded panel. I was still always getting at least half of the amps coming in (i.e. the non-shaded panel's worth), and sometimes more. The only time it knocked out "more" than the one panel was with cells completely shaded (the cardboard right on top of the cells for 100% blockage). Some amps still came in, but only about half of one panel. I don't have much that could do that on my roof (the tree and branch scenario is more likely), so I will probably start with series pairs. But if one had something big and blocky (or like on a boat where there are SO MANY things to block cells) then ....?
Maybe they have changed the Compact panels. This is the label they were showing for them. This is the label that would normally be on the back side of the panel:
On the fusing, just keep in mind a couple of things. One is that a fuse is to protect the wire. So you can't always just up the size. I think the stock solar wire is 12AWG. If it's rated at 90ºC then you could fuse it to 40 amps, so not saying you are not safe there. Just something to keep in mind when changing fuse sizes. Also, for solar, go as large as you can to save on the voltage drop of smaller fuses. Voltage drop is the enemy.
Just for example, let's say one were to put two 100 watt panels on the original Chinook wire. Let's say you added ten feet of wire to get to the new second panel. That would be around 32' of 12 AWG, one way. Now let's say you run them in series and have 5 amps at 16 volts trundling along. The voltage drop would be 4.4% (not counting any additional wire such as battery jumpers). That would make your 16 volts into about 15.3 volts. But we also have a solar controller in there. So let's say you set your solar controller to absorb at 14.4 volts (that's a common spec for a lead acid battery in absorb). Now you have around 15' to the controller, so that voltage drop is a bummer, but doesn't actually affect your battery charging specs. It only causes you to lose some power that will never get to the controller.
But now the controller puts out 14.4 volts (if it's 77ºF) and that goes 17' to the batteries on the Chinook stock wire. That's about 2.3% voltage drop on that leg (controller to batteries). That means the 14.4 volts your batteries want (and that you set into the controller) will actually be 14.06 volts (about). That's a big difference for batteries.
None of this may matter to you. Many people just plan on replacing batteries every year or two (obviously buy relatively cheap ones) and that is a fine plan if it suits your attitude and the availability of batteries to you. Just something to be aware of.
Admittedly, I'm on the opposite end of the spectrum. I rely on my batteries for boondocking all the time, and I hate re-buying things. So I have my system set up for minimum voltage drop, have a temperature compensated controller, etc. But that's not the only way. The only time it kind of bums me out is if someone thinks they are doing "Way A," but without realizing it are actually doing "Way B." That can lead to frustration.
On the series pairs: I too always read the wisdom of not doing series if there might be any shading. However it was attractive to me for a couple of reasons: You can have longer and thinner wires (less voltage drop at higher voltage), fewer wires, and (theoretically at least), the panels will "wake up" sooner and "go to bed" later. The first advantage is huge for ground panels, as you can have a longer thinner tether for the same result. But also it's fairly easy to put them in the sun so not much to lose by going series and everything to gain.
But what about roof panels? Well, I took a pair of matching panels (135 watts each, 17.6 volts vmp) and set them out on a summer day at around noon. So good, predictable sun. I set them flat on the ground, like an RV roof would be. I hooked them up to my battery monitor and the display on my MPPT controller so I could get good info. I started up some big loads so the controller would have reason to give me everything the panels could. Then I started in with the shade. Various things I tried were thin branches about 15' away, falling in a line or two over the panels, large deciduous trees a few hundred feet away shading either small amounts of one panel or up to a third or half of one panel (more blob like shape), and then finally l placed a piece of cardboard over one or more cells on one panel.
Interestingly, the branches and the big far away trees only knocked out either part or all of the shaded panel. I was still always getting at least half of the amps coming in (i.e. the non-shaded panel's worth), and sometimes more. The only time it knocked out "more" than the one panel was with cells completely shaded (the cardboard right on top of the cells for 100% blockage). Some amps still came in, but only about half of one panel. I don't have much that could do that on my roof (the tree and branch scenario is more likely), so I will probably start with series pairs. But if one had something big and blocky (or like on a boat where there are SO MANY things to block cells) then ....?