Re: 3 electrical systems
Posted: January 16th, 2019, 12:24 pm
Okay, I just read through the manual. I'm not going to organize this because it would take forever, but I wrote my thoughts as I went along so that's how they are presented. They are below the numbered points which I tried to organize a little bit. I wouldn't use this for solar charging myself, as I understand it from a quick read-through. Why?
1) Battery charging voltages are not adjustable. You get one preset for your battery type and have to hope it matches (would not match my Lifelines).
2) You cannot put solar panels in series (voltage limit is only 23 volts). Even if you go parallel on the roof (which is fine, just means larger wire), I really really like to go series for ground panels because you can have a longer/thinner wire to set them in an advantageous place. (I get such good use out of my ground panels that I could not give that up.)
3) The 20 amps of solar charging is cut down to ~15 amps if the temperature is over 86ºF. That's okay if you only have 200 watts of panels, but no more (my solar controller will max out its 15 amps in full sun with 200 watts of panels). I forget your planned solar panel array size and type.
4) I don't see a very good display unless I'm missing it.
5) Their wire sizing chart allows for 10% voltage drop. Obviously you wouldn't do that, but it just makes me wonder what they are thinking, unless I'm misunderstanding.
6) Temperature compensation factor is not adjustable (again, fine if it happens to match your batteries).
As far as alternator charging I would have to compare it to other units to see how they compare. Maybe no other ones are better (and once you add the Smart Pass I'm not even sure which adjustment and charge factors from the SA250 apply?). I'm very familiar with solar controllers so that's easier for me to judge.
I guess this seems to me like those bookshelf stereos back in the day where they were never as good as components for all but the most quick and simple setups. Where might I use this? Well, I probably never would, but maybe I could see it for something like a Jeep with super limited space and where you would never put in anything more involved anyway.
Here are my notes from as I read along in the instructions. Some of these things I'm obviously just wondering about and don't know or couldn't tell.
*********
Temperature compensated charge voltage
The D250SA optimises the charge voltage by increasing the charge voltage at temperatures below 25°C/77°F and reducing it at temperatures higher than 25°C/77°F. The functions is always active.
Can the compensation factor be adjusted to match that of the batteries? Answer: No.
Does this apply to the Smart Pass too? I can't tell.
Optimised charging of AGM batteries
The D250SA can provide a suitable charging voltage for optimal charging of AGM (Absorbent Glass Mat) batteries, which require a higher charge voltage than other types of lead-acid battery. The installation section describes how the D250SA needs to be connected in order to activate the AGM battery function.
Is this adjustable? Answer, no, it is set at 23 mV/°C from 25°C/77°F. If this matches your batteries then great. If not you can't change it. This is "by what factor it adjusts the charging for every degree above and below 77F"
Also is the Smartpass is temperature compensated?? This might be something you would want if you are doing a lot of alternator charging (but one thing I don't know is if other ones, like Sterling, are temperature compensated from the start/alternator). Or does this somehow use the 250 temp comp? Voltage settings?
• SMARTPASS 120 supplies consumers from the alternator instead of from the service battery while the service battery is charging, which permits faster charging.
Not sure why this is necessary? All power has to come from somewhere, so normally while driving it's consumers from house bank and charge from start/alternator (and solar if sun it out). Why is it better to have both coming from alternator/start bank? Seems like it would just reduce charging by that amount? Or put more load on alternator? Maybe I'm missing something. Or maybe this really applies to something like a Jeep with a 60ah house bank and a huge alternator, where the house bank can't keep up?
Battery guard
SMARTPASS 120 disconnects consumers when the service battery voltage is low in order to avoid deep discharge, which would damage the battery. The consumers are reconnected after the service battery voltage has increased. Connect critical consumers directly to the service battery so they will not be disconnected if the voltage falls to lower than 11.5V.
So in order to use this you connect some of your house loads through the start bank? I'm not sure I get this.
• Start assistance
SMARTPASS 120 automatically connects the service battery to the starter battery for 10 sec to assist, if the starter battery on its own is unable to start the engine. After the start assistance func- tion has been activated, SMARTPASS 120 will display a fault indication until starting has been achieved without using the start assistance function.
Make sure you can see this indication and look for it often! Some of the old Sure Power combiners had an automatic function like this and it "allowed" people to go for years without knowing their start battery had failed. I would rather this not exist and so I know obviously that my start battery is not up to the task and I manually combine then fix it at first opportunity.
• Separation of the starter battery and the service battery
SMARTPASS 120 separates the starter battery from the service battery when the engine is not running.
Is this magnetic latching, or? If not, what type is it and does it induce any voltage drop? I couldn't find this but admittedly I was nearly skimming.
The cable size chart does not specify one-way or round trip wiring. I would guess one-way since most vehicles use chassis ground for the return trip so there is only one wire (plus two jumper bits in the negative run). But I question their math as they are saying 1AWG cable for up to 140 amps on a 30 foot wire? Let's check that voltage drop: That's 10% voltage drop. That is beyond unacceptable for something like this. I mean look at it this way: You carefully buy a product that will absorb charge your batteries at a carefully set 14.4 volts. Then you reduce that by 10%. Now you are "charging" your batteries at 13 volts…. No. Maybe there is a voltage sense wire? [Note, I don't see a voltage sense wire]
On the solar part, maximum input voltage is 23 volts. So that means no series connected panels whatsoever. That's not too bad on the roof but kind of cuts out ground panels with any meaningful length of wire. Why so low?
Okay, here we get to the meat of it. This is what cut it out of my consideration list before (friend was asking if it was a good idea): Battery charging parameters are not adjustable. Their "AGM" profile, for example, is not correct for any of the parameters of my Lifeline batteries. Does it fit yours? Do you ever plan to change? I just think this is a bad idea in general. Why have something so fancy and then not be able to set it correctly (unless you find batteries that happen to fit their parameters). They have "AGM" at absorb 14.7 volts and float 13.6 volts. Lifeline AGM calls for 14.4 and 13.3 (tenths are a big deal in battery charging).
Also a key thing in charging lead acid batteries, is… what mechanism does the charger use to decide when to stop absorbing (ideally this is exactly when the battery is full; different chargers use different ways). I don't see them saying how, but I see a "timeout" of 12 hours (you would normally absorb for something like 1-4 hours). How are they deciding when to go from absorb to float?
It only works down to -4F. Probably not an issue but something to note if you are up north in winter. BUT more importantly, at 86ºF the 250 is reduced to 16 amps. That could be an issue for solar power, as 86 is not that hot. If you are not going to have more than 200 watts of solar then it might not matter so much. I don't think that affects alternator power (not mentioned in 120 specs). That wouldn't work for me for solar though.
1) Battery charging voltages are not adjustable. You get one preset for your battery type and have to hope it matches (would not match my Lifelines).
2) You cannot put solar panels in series (voltage limit is only 23 volts). Even if you go parallel on the roof (which is fine, just means larger wire), I really really like to go series for ground panels because you can have a longer/thinner wire to set them in an advantageous place. (I get such good use out of my ground panels that I could not give that up.)
3) The 20 amps of solar charging is cut down to ~15 amps if the temperature is over 86ºF. That's okay if you only have 200 watts of panels, but no more (my solar controller will max out its 15 amps in full sun with 200 watts of panels). I forget your planned solar panel array size and type.
4) I don't see a very good display unless I'm missing it.
5) Their wire sizing chart allows for 10% voltage drop. Obviously you wouldn't do that, but it just makes me wonder what they are thinking, unless I'm misunderstanding.
6) Temperature compensation factor is not adjustable (again, fine if it happens to match your batteries).
As far as alternator charging I would have to compare it to other units to see how they compare. Maybe no other ones are better (and once you add the Smart Pass I'm not even sure which adjustment and charge factors from the SA250 apply?). I'm very familiar with solar controllers so that's easier for me to judge.
I guess this seems to me like those bookshelf stereos back in the day where they were never as good as components for all but the most quick and simple setups. Where might I use this? Well, I probably never would, but maybe I could see it for something like a Jeep with super limited space and where you would never put in anything more involved anyway.
Here are my notes from as I read along in the instructions. Some of these things I'm obviously just wondering about and don't know or couldn't tell.
*********
Temperature compensated charge voltage
The D250SA optimises the charge voltage by increasing the charge voltage at temperatures below 25°C/77°F and reducing it at temperatures higher than 25°C/77°F. The functions is always active.
Can the compensation factor be adjusted to match that of the batteries? Answer: No.
Does this apply to the Smart Pass too? I can't tell.
Optimised charging of AGM batteries
The D250SA can provide a suitable charging voltage for optimal charging of AGM (Absorbent Glass Mat) batteries, which require a higher charge voltage than other types of lead-acid battery. The installation section describes how the D250SA needs to be connected in order to activate the AGM battery function.
Is this adjustable? Answer, no, it is set at 23 mV/°C from 25°C/77°F. If this matches your batteries then great. If not you can't change it. This is "by what factor it adjusts the charging for every degree above and below 77F"
Also is the Smartpass is temperature compensated?? This might be something you would want if you are doing a lot of alternator charging (but one thing I don't know is if other ones, like Sterling, are temperature compensated from the start/alternator). Or does this somehow use the 250 temp comp? Voltage settings?
• SMARTPASS 120 supplies consumers from the alternator instead of from the service battery while the service battery is charging, which permits faster charging.
Not sure why this is necessary? All power has to come from somewhere, so normally while driving it's consumers from house bank and charge from start/alternator (and solar if sun it out). Why is it better to have both coming from alternator/start bank? Seems like it would just reduce charging by that amount? Or put more load on alternator? Maybe I'm missing something. Or maybe this really applies to something like a Jeep with a 60ah house bank and a huge alternator, where the house bank can't keep up?
Battery guard
SMARTPASS 120 disconnects consumers when the service battery voltage is low in order to avoid deep discharge, which would damage the battery. The consumers are reconnected after the service battery voltage has increased. Connect critical consumers directly to the service battery so they will not be disconnected if the voltage falls to lower than 11.5V.
So in order to use this you connect some of your house loads through the start bank? I'm not sure I get this.
• Start assistance
SMARTPASS 120 automatically connects the service battery to the starter battery for 10 sec to assist, if the starter battery on its own is unable to start the engine. After the start assistance func- tion has been activated, SMARTPASS 120 will display a fault indication until starting has been achieved without using the start assistance function.
Make sure you can see this indication and look for it often! Some of the old Sure Power combiners had an automatic function like this and it "allowed" people to go for years without knowing their start battery had failed. I would rather this not exist and so I know obviously that my start battery is not up to the task and I manually combine then fix it at first opportunity.
• Separation of the starter battery and the service battery
SMARTPASS 120 separates the starter battery from the service battery when the engine is not running.
Is this magnetic latching, or? If not, what type is it and does it induce any voltage drop? I couldn't find this but admittedly I was nearly skimming.
The cable size chart does not specify one-way or round trip wiring. I would guess one-way since most vehicles use chassis ground for the return trip so there is only one wire (plus two jumper bits in the negative run). But I question their math as they are saying 1AWG cable for up to 140 amps on a 30 foot wire? Let's check that voltage drop: That's 10% voltage drop. That is beyond unacceptable for something like this. I mean look at it this way: You carefully buy a product that will absorb charge your batteries at a carefully set 14.4 volts. Then you reduce that by 10%. Now you are "charging" your batteries at 13 volts…. No. Maybe there is a voltage sense wire? [Note, I don't see a voltage sense wire]
On the solar part, maximum input voltage is 23 volts. So that means no series connected panels whatsoever. That's not too bad on the roof but kind of cuts out ground panels with any meaningful length of wire. Why so low?
Okay, here we get to the meat of it. This is what cut it out of my consideration list before (friend was asking if it was a good idea): Battery charging parameters are not adjustable. Their "AGM" profile, for example, is not correct for any of the parameters of my Lifeline batteries. Does it fit yours? Do you ever plan to change? I just think this is a bad idea in general. Why have something so fancy and then not be able to set it correctly (unless you find batteries that happen to fit their parameters). They have "AGM" at absorb 14.7 volts and float 13.6 volts. Lifeline AGM calls for 14.4 and 13.3 (tenths are a big deal in battery charging).
Also a key thing in charging lead acid batteries, is… what mechanism does the charger use to decide when to stop absorbing (ideally this is exactly when the battery is full; different chargers use different ways). I don't see them saying how, but I see a "timeout" of 12 hours (you would normally absorb for something like 1-4 hours). How are they deciding when to go from absorb to float?
It only works down to -4F. Probably not an issue but something to note if you are up north in winter. BUT more importantly, at 86ºF the 250 is reduced to 16 amps. That could be an issue for solar power, as 86 is not that hot. If you are not going to have more than 200 watts of solar then it might not matter so much. I don't think that affects alternator power (not mentioned in 120 specs). That wouldn't work for me for solar though.